Hej Abdalla,
thanks for sharing your experience.
I have been digging into the soft motor business recently,
still working on a patch to allow the forward of motor status
(the .MSTA field) into other records.
Back to your problem:
There may be a timing problem of some kind,
between the poller towards the Galil and the soft “motor poller”.
(This is my limited understanding).
However, in order to understand your situation better,
could you run a camonitor/pvmonitor on the following fields:
.VAL
.RBV
.DMOV
for all 4 motors:
The 2 physical motors and the 2 logical ones ?
Tech-talk <tech-talk-bounces at aps.anl.gov> on behalf of Abdalla Ahmad via Tech-talk <Tech-talk at aps.anl.gov>
Reply to: Abdalla Ahmad <Abdalla.Ahmad at sesame.org.jo>
Date: Thursday, 4 January 2024 at 13:00
To: "tech-talk at aps.anl.gov" <Tech-talk at aps.anl.gov>
Subject: Behavior of the soft motor's DINP field
Hi
I am trying to implement a simple kinematics system for a standard slit motion, where we have the kinematics equation as:
Gap = A + B
Center = (A – B)/2
I used the motor record’s soft motor implementation which has an example
here. The actual motor controller is Galil DMC based on the Galil EPICS driver, the kinematics is working fine but there might be some kind of a bug in the RBV value of the soft motors. If you were to move any motor whether
actual or soft, the transform record starts calculating and updates the soft motor RBV accordingly, but the soft motor stops before reaching the actual calculated position due to the fact that the DINP field receives 1 if both motors are done moving (DMOV
= 1). For example it is supposed to reach 5 mm but it reaches to 4.97 for example. The error might not be that much but it gets accumulated in each motion. I tried to investigate more and I found the following:
Removing the DINP link value “fixes” the behavior? I am not sure if it is fixed or not but the soft motors reach their corresponding values.
I remembered that we are configuring our Galil controllers on a 8 ms update rate. I set the update rate to slower values and the issue can be resolved.
I looked into the soft motor record’s source code and I noticed that the DINP value is mapped into 3 values: SOFTMOVE = 0, HARDMOVE = 1 and DONE = 2. I am not sure exactly what those mean, but I tried setting these values to the DINP field
but it did not work, it seems there is a certain logic happening inside the record that behaves differently on each value.
This issue can problematic because the error in the position can be accumulated with each motion, also I am not sure how the SSCAN module will behave in this case. Any insight is really appreciated.
Best Regards,
Abdalla Al-Dalleh
Control Engineer
SESAME (Synchrotron-light for Experimental Science and Applications in the Middle East)
P.O. Box 7, Allan 19252, Jordan
Tel: +96253511348 , ext. 265
Fax: +96253511423
abdalla.ahmad at sesame.org.jo
www.sesame.org.jo