Yes. I added.
Printf is show the Raw Data value and calibration factor.
And, I using the internal power supply +-12v. J1,J2 jumper settings is
equal.
I don't know more about the interrupt vector.
ipacAddXy9660("0000,4 A=2,800000")
initIp330("IP330_1",0,0,"D","-5to5",0,15,4)
interrupt vector value was not 4 then IP330 was print error message about
vector.
And AVME9670 link LED was not blink.
Best regards.
Geon-Yeong.
-----Original Message-----
Sent: Monday, June 03, 2013 11:54 AM
To: Geon-Yeong Mun; [email protected]
Subject: RE: IP330 modules question
Are the debugging print statements you show ones that you have added?
What voltage source are you using for the IP330, the internal +-12V, or
external +-15V?
Are you sure that interrupt vector 4 is correct?
The VoltCALLO values seem to be jumping all over the place in the
calibration routine.
behalf of Geon-Yeong Mun [[email protected]]
Sent: Sunday, June 02, 2013 9:19 PM
To: [email protected]
Subject: IP330 modules question
Hi all.
I tried to run IP300 module, and read the Analog data.
All Raw data(16ch Diff mode) are displayed as shown below. This data's
source is 5 voltage.
Data: 65535
Data: 65535
Data: 50845
Data: 33453
Data: 65535
Data: 65535
Data: 33454
Data: 33453
Data: 33450
Data: 65535
Data: 65535
Data: 33452
Data: 33452
Data: 33453
Data: 65535
Data: 65535
Data: 33452
Data: 33453
Data: 65535
Data: 65535
Data: 65535
Data: 33451
Data: 33454
Data: 65535
Data: 65535
Data: 65535
This repeating pattern is the 33453 and 65535
Are you known about this?
Development environment
Epics base: 3.14.12.3
Target os : vxWorks 6.9
Hardware : AVME9670, IP330A
Modules : ipac 2.11, ip330
Best regards.
Geon-Yeong
boot device : geisc
unit number : 0
processor number : 0
host name : gymun-evr
file name : /home/work/image/vxWorks
inet on ethernet (e) : 141.223.48.53:ffffff00
host inet (h) : 141.223.48.51
gateway inet (g) : 141.223.48.99
user (u) : work
ftp password (pw) : work
flags (f) : 0x0
target name (tn) : evrTest
startup script (s) : /home/work/st.vxWorks.evr
Loading... 2354032
Starting at 0x100000...
Loading symbol table from gymun-evr:/home/work/image/vxWorks.sym ...done
VxWorks
Copyright 1984-2013 Wind River Systems, Inc.
CPU: Motorola MVME6100-0173 - MPC 7457
Runtime Name: VxWorks
Runtime Version: 6.9
BSP version: 6.9/0
Created: May 23 2013, 18:22:53
ED&R Policy Mode: Deployed
WDB Comm Type: WDB_COMM_END
WDB: Ready.
Executing startup script '/home/work/st.vxWorks.evr'...
ipAttach(1,"geisc")
value = 0 = 0x0
ifconfig("geisc1 inet 192.168.10.131 netmask 255.255.255.0 up")
value = 0 = 0x0
tyBackspaceSet(0177)
value = 127 = 0x7f
#ld < mrf.munch
ld < mrfTest.munch
value = 72237072 = 0x44e4010
# env setting
epicsEnvSet("ENGINEER","Geon-Yeong Mun")
value = 0 = 0x0
epicsEnvSet("LOCATION","TestLab")
value = 0 = 0x0
epicsEnvSet("EPICS_CA_MAX_ARRAY_BYTES","1000000")
value = 0 = 0x0
epicsEnvSet("EPICS_TS_NTP_INET","141.223.48.51")
value = 0 = 0x0
#dbLoadDatabase("dbd/mrf.dbd",0,0)
#mrf_registerRecordDeviceDriver(pdbbase)
dbLoadDatabase("dbd/mrfTest.dbd",0,0)
value = 0 = 0x0
mrfTest_registerRecordDeviceDriver(pdbbase)
value = 0 = 0x0
# IRQ 3: EVR
# IRQ 4: AVME9670
# EVG(A24)
#mrmEvgSetupVME("EVG1",2,0x00050000,4,0xc0)
#mrmEvgSetupVME("EVG1",2,0x00000000,4,0xc0)
# sysBusToLocalAdrs(0x0d,0x00100000,&a)Can't reg
ister 'system' comm
and -- no command i# EVR(A24)nterpreter
available.
#mrmEvrSetupVME("EVR1",5,0x00100000,3,0x26)
#mrmEvrSetupVME("EVR1",5,0x00200000,4,0x24)
#mrmEvrSetupVME("EVR1",5,0x08000000,3,0x26)
mrmEvrSetupVME("EVR1",2,0x00000000,3,0x26)
Setting up EVR in VME Slot 2
Found vendor: 00000eb2 board: 455246e6 rev.: 00000000
EVR check. EVR-230 'EVR1' slot 2
FPGA version... 0006
Found SFP Strangeness ffffffff
FWVersVME64 ion 0x12000006Out FP:
7 FPUNIV:4 RB:Found version 6
16 IFP:2
Using IRQ 35:38EVR FIFO task start
value = 0 = 0x0
# sysBusToLocalAdrs(0x0d,0x00280000,&k)
# sysBusToLocalAdrs(0x0d,0x00300000,&k)
# 0xF8 : 7C00000
# ACROMAG AVME9670
Now finish parsing.... A=2,800000
AVME-IP: init success...1
value = 0 = 0x0
# ACROMAG IP330
# string : portName
# int carrierID
# int SlotID
# string type : "D" or "S" for differential or single-ended
# string range
# int firstChan
# int lastChan
# int interruptVector
#initIp330("IP330_1",0,0,"D","-5to5",0,15,4)
value = 0 = 0x0
configIp330("IP330_1",3,"Input",1000,60)
########### CALIBRATION ########
CH 00
Corrected_Count: 1.019773
Ideal_Volt_Span: 10.000000
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64941.968750
CountCALLO: 33451.968750
drvIp330::calibrate channel 0 adj_slope 1.019773e+00 adj_offset
-1.319316e+03
CH 01
Corrected_Count: 1.018058
m: 0.000155
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64941.718750
CountCALLO: 33398.687500
drvIp330::calibrate channel 1 adj_slope 1.018058e+00 adj_offset
-1.211921e+03
CH 02
Corrected_Count: -54.189974
m: -0.008269
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.406250
CountCALLO: 65535.000000
drvIp330::calibrate channel 2 adj_slope -5.418997e+01 adj_offset
-6.613969e+04
CH 03
Corrected_Count: -54.178546
m: -0.008267
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.281250
drvIp330::calibrate channel 3 adj_slope -5.417855e+01 adj_offset
-6.613982e+04
CH 04
Corrected_Count: 2.016120
m: 0.000308
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64941.843750
CountCALLO: 49013.906250
drvIp330::calibrate channel 4 adj_slope 2.016120e+00 adj_offset
-3.276091e+04
CH 05
m: -0.008269
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
drvIp330::calibrate channel 5 adj_slope -5.418997e+01 adj_offset
-6.613969e+04
CH 06
Corrected_Count: 1.019771
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.250000
CountCALLO: 33452.187500
drvIp330::calibrate channel 6 adj_slope 1.019771e+00 adj_offset
-1.319471e+03
CH 07
Corrected_Count: 1.021627
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 33509.125000
drvIp330::calibrate channel 7 adj_slope 1.021627e+00 adj_offset
-1.434795e+03
CH 08
Corrected_Count: -54.149996
m: -0.008263
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
drvIp330::calibrate channel 8 adj_slope -5.415000e+01 adj_offset
-6.614013e+04
CH 09
Corrected_Count: 1.019775
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 33451.906250
drvIp330::calibrate channel 9 adj_slope 1.019775e+00 adj_offset
-1.319317e+03
CH 10
Corrected_Count: 1.063591
m: 0.000162
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.437500
CountCALLO: 34749.781250
drvIp330::calibrate channel 10 adj_slope 1.063591e+00 adj_offset
-3.940948e+03
CH 11
Corrected_Count: 11.663407
m: 0.001780
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.625000
CountCALLO: 62189.343750
drvIp330::calibrate channel 11 adj_slope 1.166341e+01 adj_offset
-5.937987e+04
CH 12
Corrected_Count: 1.019800
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64941.875000
CountCALLO: 33452.718750
drvIp330::calibrate channel 12 adj_slope 1.019800e+00 adj_offset
-1.320927e+03
CH 13
Corrected_Count: 1.019208
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.031250
CountCALLO: 33434.593750
drvIp330::calibrate channel 13 adj_slope 1.019208e+00 adj_offset
-1.284147e+03
CH 14
Corrected_Count: -54.147143
m: -0.008262
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64941.937500
drvIp330::calibrate channel 14 adj_slope -5.414714e+01 adj_offset
-6.614017e+04
CH 15
Corrected_Count: 1.020357
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 33470.000000
drvIp330::calibrate channel 15 adj_slope 1.020357e+00 adj_offset
-1.355746e+03
CH 00
Corrected_Count: -54.158558
m: -0.008264
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.062500
drvIp330::calibrate channel 0 adj_slope -5.415856e+01 adj_offset
-6.614004e+04
CH 01
Corrected_Count: -54.144290
m: -0.008262
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64941.906250
drvIp330::calibrate channel 1 adj_slope -5.414429e+01 adj_offset
-6.614020e+04
CH 02
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64941.812500
CountCALLO: 33451.875000
drvIp330::calibrate channel 2 adj_slope 1.019775e+00 adj_offset
-1.319286e+03
CH 03
Corrected_Count: -142.248682
m: -0.021705
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 65168.000000
drvIp330::calibrate channel 3 adj_slope -1.422487e+02 adj_offset
-6.539836e+04
CH 04
Corrected_Count: 1.678135
m: 0.000256
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 45805.968750
drvIp330::calibrate channel 4 adj_slope 1.678135e+00 adj_offset
-2.627953e+04
CH 05
Corrected_Count: 1.019750
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.156250
CountCALLO: 33451.468750
drvIp330::calibrate channel 5 adj_slope 1.019750e+00 adj_offset
-1.318114e+03
CH 06
Corrected_Count: -54.175690
m: -0.008267
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
drvIp330::calibrate channel 6 adj_slope -5.417569e+01 adj_offset
-6.613985e+04
CH 07
Corrected_Count: 11.856519
m: 0.001809
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 62233.593750
drvIp330::calibrate channel 7 adj_slope 1.185652e+01 adj_offset
-5.946988e+04
CH 08
Corrected_Count: -54.187117
m: -0.008268
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.375000
drvIp330::calibrate channel 8 adj_slope -5.418712e+01 adj_offset
-6.613972e+04
CH 09
m: -0.008267
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
drvIp330::calibrate channel 9 adj_slope -5.417569e+01 adj_offset
-6.613985e+04
CH 10
Corrected_Count: 1.019763
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 33451.718750
drvIp330::calibrate channel 10 adj_slope 1.019763e+00 adj_offset
-1.318747e+03
CH 11
Corrected_Count: -66.207363
m: -0.010102
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64941.781250
CountCALLO: 65426.812500
drvIp330::calibrate channel 11 adj_slope -6.620736e+01 adj_offset
-6.592174e+04
CH 12
Corrected_Count: 1.014113
m: 0.000155
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 33276.187500
drvIp330::calibrate channel 12 adj_slope 1.014113e+00 adj_offset
-9.641977e+02
CH 13
Corrected_Count: 1.019767
m: 0.000156
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 33451.843750
drvIp330::calibrate channel 13 adj_slope 1.019767e+00 adj_offset
-1.318999e+03
CH 14
Corrected_Count: -54.164267
m: -0.008265
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALHI: 64942.125000
drvIp330::calibrate channel 14 adj_slope -5.416427e+01 adj_offset
-6.613997e+04
CH 15
Corrected_Count: 9.344492
m: 0.001426
Gain: 1.000000
VoltCALHI: 4.900000
VoltCALLO: 0.000000
CountCALLO: 61505.375000
drvIp330::calibrate channel 15 adj_slope 9.344492e+00 adj_offset
-5.799871e+04
value = 0 = 0x0
Data: # EVG db
#dbLoadRecords("db/vme-evg230.db", "SYS=TST, D=evg:1, EVG=EVG1")
64694
# BNL specific timing sequence constructor
#dbLoadRecords("db/nsls2-inj-seqs.db","LN=LN-TS, BR=BR-TS, INJ=TST,
EVG=evg:1, SEQ=SoftSeq:0")Data:
# EVR
33452dbLoadRecords("db/evr-vmerf-230.db","SYS=TST, D=evr:1, EVR=EVR1")
Data: 33451
Data: 33452
Data: 33454
Data: 33453
Data: 33452
Data: 3value = 0 = 0x0
# IP330
dbLoadTemplate("db/ip330Scan.substitutions")
3448
Data: 36040
Data: 64906
Data: 63022
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 41509
Data: 33451
Data: 33453
Data: 33452
Data: 33452
Data: 33451
Data: 33451
Data: 33452
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 33456
Data: 33451
Data: 33451
Data: 33452
Data: 33451
Data: 33453
Data: 33451
Data: 33453
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 33454
Data: 33452
Data: 334value = 520 = 0x0
dbLoadRecords("db/iocAdminVxWorks.db", "IOC=evrTest")Data:
33452
Data: 33452
Data: 3345value = 0 = 0x0
iocInit()Data:
Starting iocInit
65535####
###################Data: ##############65535###############
## EPICS65535 R3.14.12.3 $Da
te: Mon 2012-12-17 Data: 14:11:47 -060065535$
## EPICS Base
built May 14 2013
Data: 45663
Data: 33452
Data: 33452
Data: 33452
Data: 33451
Data: 33452
Data: 33453
Data: 33451
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 65535
Data: 33456
Data: 33451
Data: 33451
Data: 33452
- RE: IP330 modules question Mark Rivers
- IP330 modules question Geon-Yeong Mun
EPICS cross compile with buildroot problems Tom Slejko
<2013>
<2013>
